==Overview== | |||
[[File:Gen2.jpg|thumb|tesla gen2 ac charger]] | |||
[[File:Tesla gen2 xray.png|thumb|Tesla Gen2 X-Ray]] | |||
The Tesla GEN2 on-board charger (OBC) is a single/three phase 10kW AC charger that was fitted in the Model S from approx. Oct2013<ref>https://teslamotorsclub.com/tmc/posts/6560948/</ref> until it was replaced in the 2016 'facelift' model with GEN3. It was the first Tesla OBC capable of fully utilizing external 3-phase AC; [[Tesla Model S GEN1 Charger|previous Tesla OBCs]] lacked the external wiring for three phases. | |||
One or two GEN2 chargers are installed beneath the rear seats in the Model S for AC charging. | |||
The charger is made up of three 3.3 kw modules, each sitting on a liquid cooling plate. This assembly enables both single and multi phase AC charging. | |||
Tesla gen2 charger weighs 16kg!!! Surprisingly low for such a bulky item | |||
===Output Voltage Range=== | |||
{| class="wikitable" style="background-color:#ffffcc;" cellpadding="10" | |||
"[https://openinverter.org/forum/viewtopic.php?f=10&t=78&p=9994#p9994 Running a Tesla charger at much under 200v dc will cause it to explode. Yes I know the label says 50 to 450v but it lies. Yes I blew one up discovering this.]" | "[https://openinverter.org/forum/viewtopic.php?f=10&t=78&p=9994#p9994 Running a Tesla charger at much under 200v dc will cause it to explode. Yes I know the label says 50 to 450v but it lies. Yes I blew one up discovering this.]" | ||
===Supported Tesla Part Numbers (TPN)=== | |||
It has been found that early revision units will not work with the OI control boards.<ref>https://openinverter.org/forum/viewtopic.php?t=932</ref> | |||
TPNs to avoid: | |||
*1014963-05-B and 1014963-05-C | |||
TPNs tested and known good: | |||
*1014963-00-C/E/F/J/K/L | |||
**1014963-00-C <ref>https://openinverter.org/forum/viewtopic.php?p=34710#p34710 and also by Lars on June 25th 2024</ref> | |||
**1014963-00-G is likely also good, just wasn't mentioned by name in the referenced thread | |||
=== Supported Software Revisions === | |||
At this time, it is not known why but it appears that some firmware revisions of this charger will have problems with maintaining a steady charge. Symptoms of this can be either surging (current goes up, drops to near zero, then surges back) or modules coming online singly followed by all modules going offline, repeat forever. In either case, charge power will be limited. We do not yet know what, exactly, is causing this. However, it is confirmed that swapping charger units but keeping the OI control board can produce working results. | |||
===Cooling=== | |||
The direction of flow in the cooling plate does not seem to matter.<ref>https://openinverter.org/forum/viewtopic.php?p=2030#p2030</ref> The charger should likely be on the same cooling loop as the batteries themselves. This coolant loop should be separate from the loop with the motor and inverter (they get far too hot.) Limited testing (esp 110V, 1kw) can be done without the coolant lines hooked up. However, it would be unwise to attempt 10kw charging for any length of time without liquid cooling. | |||
== Replacement | ==Replacement Control Boards== | ||
Replacement control board https://github.com/damienmaguire/Tesla-Charger | |||
v5 kit: https://www.evbmw.com/index.php/evbmw-webshop/tesla-boards/tesla-gen-2-charger-logic-board-kit | v5 kit: https://www.evbmw.com/index.php/evbmw-webshop/tesla-boards/tesla-gen-2-charger-logic-board-kit | ||
| Line 14: | Line 45: | ||
v5 partially built board: https://www.evbmw.com/index.php/evbmw-webshop/tesla-boards/tesla-gen-2-charger-logic-board-partially-built | v5 partially built board: https://www.evbmw.com/index.php/evbmw-webshop/tesla-boards/tesla-gen-2-charger-logic-board-partially-built | ||
github: https://github.com/damienmaguire/Tesla-Charger | |||
== Charger | === Charger Connections === | ||
[[File:Tesla Charger Logic connections.jpg|none|thumb| | [[File:Tesla Charger Logic connections.jpg|none|thumb|607x607px| | ||
!A1 | !A1 | ||
| Line 28: | Line 60: | ||
!B3 | !B3 | ||
!B4 | !B4 | ||
!B5 | ! B5 | ||
!B6 | !B6 | ||
| Line 46: | Line 78: | ||
!A6 | !A6 | ||
!A7 | !A7 | ||
! A8 | |||
!A9 | !A9 | ||
!A10 | !A10 | ||
!B7 | !B7 | ||
| Line 61: | Line 93: | ||
|D2 - 3p | |||
| GND | |||
|GND | |||
| Line 70: | Line 102: | ||
]] | The outputs will not output 12v, they are low side switches. If you require a 12v ac present signal then use a relay with its coil switched from the relevant pin. [https://raw.githubusercontent.com/damienmaguire/Tesla-Charger/master/V5/Charger_Gen2_V5aB3%20-%20Schematic.pdf wiring diagram][[File:AC DC Connections.jpg|left|thumb|600x600px]]]] | ||
=== Connector part numbers === | ====Connector part numbers==== | ||
AC and DC power connections | AC and DC power connections (Molex Sabre series): | ||
*housing: 044441-2006 | |||
*pins: 043375-3001 (18-20AWG), 043375-0001 (14-16AWG) | |||
Logic connectors (Molex MX150L series): | |||
*housing: 10-way 19418-0014, 12-way 19418-0026 | |||
*pins: 33012-2002 (18-20AWG), 33012-2001 (14-16AWG) | |||
=== Replacement board connectors === | |||
If you can, desolder the 24 pin SMD connector from the OEM control board; otherwise, order the 24 pin connector from Mouser, whose P/N is: | |||
==== | * [https://www.mouser.com/ProductDetail/JST-Automotive/SM24B-CPTK-1A-TBL?qs=wBn5QRdTcLhQ%2FCp3E8a%2FyA%3D%3D SM24B-CPTK-1A-TB(L)] | ||
# Charger_gen2_v5.hex https://github.com/damienmaguire/Tesla-Charger/tree/master/V5/Software/Binary | |||
# | The 30 pin connector is very difficult to desolder and resolder. Replacement P/Ns are: | ||
* [https://www.mouser.com/ProductDetail/Samtec/IPS1-115-01-S-D-PL?qs=PB6%2FjmICvI17nbB5SDGUsw%3D%3D IPS1-115-01-S-D-PL], SAMTEC - IPS1-115-01-S-D-PL - SOCKET, 2.54MM, 2x15WAY | |||
** NOTE: One of the pins is missing from this connector variant, but according to [https://openinverter.org/forum/viewtopic.php?p=27697&hilit=charger+pin+missing#p27697 this forum post], it's OK as long as you solder it in the correct orientation. | |||
* [https://www.mouser.com/ProductDetail/Samtec/IPS1-115-01-L-D?qs=PB6%2FjmICvI3sN4zSP4IXGw%3D%3D IPS1-115-01-L-D], SAMTEC | |||
** Has all 30 pins. | |||
===Programming=== | |||
You'll need a ST-LINK/V2 smt32 programmer. Unofficial ones are cheaply available from amazon and ebay. | |||
*ST-LINK programming utility: https://www.st.com/en/development-tools/stsw-link004.html | |||
* stm32_loader.hex https://openinverter.org/forum/viewtopic.php?f=7&t=1119 | |||
'''Two options:''' | |||
#Charger_gen2_v5.hex https://github.com/damienmaguire/Tesla-Charger/tree/master/V5/Software/Binary | |||
#openinverter style firmware https://openinverter.org/forum/viewtopic.php?t=1323 (only available via patreon for next few weeks) | |||
Click "Target --> Connect" from top menu. You want to see the screen get filled with a data dump of symbols. In the upper right of the screen you can see it identified the device. | Click "Target --> Connect" from top menu. You want to see the screen get filled with a data dump of symbols. In the upper right of the screen you can see it identified the device. | ||
| Line 92: | Line 140: | ||
In the main viewing window are multiple tabs, click the "Binary File" tab to select it. | In the main viewing window are multiple tabs, click the "Binary File" tab to select it. | ||
This will ask to open a file, you choose: "stm32_loader.hex" from | This will ask to open a file, you choose: "stm32_loader.hex" from openinverter.org, download ahead of time. This will change what shows up in the viewing window. | ||
Click "Target --> Program and Verify" from the top menu. This pops up a window, and you can probably just click "Start" on that window. This programs the STM32 chip with the stm32_loader.hex file. | Click "Target --> Program and Verify" from the top menu. This pops up a window, and you can probably just click "Start" on that window. This programs the STM32 chip with the stm32_loader.hex file. | ||
| Line 108: | Line 156: | ||
You are now done with the ST-Link USB dongle, it's no longer needed. | You are now done with the ST-Link USB dongle, it's no longer needed. | ||
Future updates can be done via | Future updates can be done via WiFi. (must have esp8266 WiFi module programed https://openinverter.org/forum/viewtopic.php?f=5&t=8 ) | ||
== External CAN bus == | === External CAN bus=== | ||
[[File:Gen2 Charger V5aB2 logic board.jpg|thumb|Gen2 Charger V5aB2 logic board with CAN wired to external pins]] | [[File:Gen2 Charger V5aB2 logic board.jpg|thumb|Gen2 Charger V5aB2 logic board with CAN wired to external pins]] | ||
The V5aB2 version of the board has no connection to the external CAN bus (V5aB3 has) but you can add it with | The V5aB2 version of the board has no connection to the external CAN bus (V5aB3 has) but you can add it with two bodge wires as shown in the picture. You will find CANH and CANL on the 3 pin header underneath the WiFi module. Route them over to CONN6 as shown. CONN2.1 (CANH) is connected to CONN6.24, CONN2.2 (CANL) to CONN6.26. | ||
Revision V5aB3 does not need this modification. On Revision V5aB3 you '''MUST''' close the solder jumper unless your charger is on an already terminated bus (that is, if the bus already has 2 termination resistors, one on each end, and measures 60 ohms with all devices powered off). If you do not use the external CAN, terminate the bus. If you have only two devices on the bus, terminate the bus. If you aren't sure, double check. '''Bus termination is important.''' | |||
If you attach to the external CAN bus, be aware that all internal CAN traffic is also seen on the external CAN bus. The following IDs are already used and mustn't used by any other device on the bus: | |||
207, 209, 217, 219, 227, 229, 237, 239, 247, 249, 327, 329, 347, 349, 357, 359, 367, 368, 369, 377, 379, 537, 539, 717, 719, | 207, 209, 20b, 217, 219, 21b, 227, 229, 22b, 237, 239, 23b, 247, 249, 24b, 327, 329, 32b, 347, 349, 34b, 357, 359, 35b, 367, 368, 369, 36b, 377, 379, 37b, 537, 539, 53b, 717, 719, 71b. | ||
==== Functionality of external CAN bus ==== | ====Functionality of external CAN bus==== | ||
With the CAN bus now available externally you can remote control your charger via CAN and also receive some values from it. The mapping is similar to the CHAdeMO CAN protocol. The feature is only available in the commercial firmware. | With the CAN bus now available externally you can remote control your charger via CAN and also receive some values from it. The mapping is similar to the CHAdeMO CAN protocol. The feature is only available in the commercial firmware. | ||
|+Charger CAN protocol | |+Charger CAN protocol - up to version 1.06.R | ||
!ID | !ID | ||
!Direction | !Direction | ||
!Byte 0 | !Byte 0 | ||
!Byte 1 | ! Byte 1 | ||
!Byte 2 | !Byte 2 | ||
!Byte 3 | !Byte 3 | ||
!Byte 4 | !Byte 4 | ||
!Byte 5 | ! Byte 5 | ||
!Byte 6 | ! Byte 6 | ||
!Byte 7 | !Byte 7 | ||
| Line 142: | Line 189: | ||
|DC voltage limit MSB | |DC voltage limit MSB | ||
|DC voltage limit LSB | |DC voltage limit LSB | ||
|DC current set point | | DC current set point | ||
|==1 enable charging | |==1 enable charging | ||
|SoC | |SoC | ||
| Line 152: | Line 199: | ||
|Version=0 | |Version=0 | ||
|Max DC voltage MSB | |Max DC voltage MSB | ||
|Max DC voltage LSB | | Max DC voltage LSB | ||
|Max DC current | |Max DC current | ||
| Line 166: | Line 213: | ||
|DC current | |DC current | ||
|''0 when off, 5 when charging'' | |''0 when off, 5 when charging'' | ||
Example: transmit "0x102 # 0 0x1 0x86 0x14 0x1 50 0 0" to enable charging up to a voltage of 390V and a DC current of 20A, report SoC of 50% | |||
after 1.06.R | {| class="wikitable" | ||
|+Charger CAN protocol - after version 1.06.R | |||
!ID | |||
!Direction | |||
!Byte 0 | |||
!Byte 1 | |||
!Byte 2 | |||
!Byte 3 | |||
!Byte 4 | |||
!Byte 5 | |||
!Byte 6 | |||
!Byte 7 | |||
| 0x102 | |||
|Receive by charger | |||
|DC voltage limit MSB | |||
|DC voltage limit LSB | |||
|DC current set point | |||
|==1 enable charging | |||
|SoC | |||
|0x108 | |||
|Transmit by charger | |||
|Version=0 | |||
|Max DC voltage MSB | |||
| Max DC voltage LSB | |||
|Max DC current | |||
|0x109 | |||
|Version=0 | |||
|DC current | |||
|0 when off, 5 when charging | |||
LR: Personally I think the data for DC voltage limit is incorrect. The above states Motorola but only when I set all signals (so not only DC voltage limit as also the start bit count (sometimes) varies) to Intel it works for me.[[File:Parameter view of commercial firmware.png|thumb|Parameter view of commercial firmware]] | |||
== | ===openinverter style charger firmware=== | ||
In addition to the open source firmware there is also | In addition to the open source firmware there is also an openinverter style firmware. It adds advanced features: | ||
* Support for the standard open inverter web interface | *Support for the standard open inverter web interface | ||
* Parameter handling as known from the inverter firmware (see picture) | *Parameter handling as known from the inverter firmware (see picture) | ||
* Spot value handling like inverter including plotting, gauges, and logging | *Spot value handling like inverter including plotting, gauges, and logging | ||
* Over the air update like inverter | *Over the air update like inverter | ||
* DC current control | *DC current control | ||
* CAN control as described above | * CAN control as described above | ||
The firmware requires the board to be flashed with [https://github.com/jsphuebner/tumanako-inverter-fw-bootloader/releases stm32_loader.hex]. An Olimex MOD-ESP8266 must be programmed with the [https://github.com/jsphuebner/esp8266-web-interface openinverter web interface]. See [https://openinverter.org/forum/viewtopic.php?f=5&t=8 | The firmware requires the board to be flashed with [https://github.com/jsphuebner/tumanako-inverter-fw-bootloader/releases stm32_loader.hex]. An Olimex MOD-ESP8266 must be programmed with the [https://github.com/jsphuebner/esp8266-web-interface openinverter web interface]. See [[Olimex MOD-WIFI-ESP8266]] and [https://openinverter.org/forum/viewtopic.php?f=5&t=8 this forum thread] for flashing instructions. With that done, future updates will happen via the web interface. | ||
The firmware will soon be fully published and is only available via patreon for now: https://www.patreon.com/openinverter | |||
====Connecting to the Web interface==== | |||
Depending on the version of your Olimex wifi dongle they are "open" or you need a password to connect. | |||
By default you can connect to the network (Access Point) and browse to: '''192.168.4.1''' | |||
By default all charger kits will have '''SSID''' : charger '''PASSWORD''' : charger123 | |||
''Note: Its recommend that you change it. Nobody wants to drive and have some joker with a phone finding this information and accessing your charger.'' | |||
'''Missing IC4 Chip''' | |||
According to [https://openinverter.org/forum/viewtopic.php?p=43750&hilit=ic4#p43750 this forum post], IC4 used to be populated with a USB to serial FTDI chip. However, on the latest boards, all settings are configured via wifi so it is no longer needed. | |||
[[File:Gen2ChargerBoard.jpg|alt=Image of Tesla Gen2 charger board with missing IC4 chip|thumb|Tesla Gen2 charger board with missing IC4 chip]] | |||
====Registration==== | |||
This step is no longer needed as the firmware will soon be published. It is already available on patreon: https://www.patreon.com/openinverter | |||
If you bought a fully assembled V5aB3 board from the EVBMW webshop you can skip this step. | If you bought a fully assembled V5aB3 board from the EVBMW webshop you can skip this step. | ||
=== Latest Software for V5 boards and later === | |||
[[Tesla Model S/Tesla Gen23 V5 Software]] | |||
==Additional Resources== | |||
Videos by Damien Maguire showing internals of the charger, CAN IDs, wiring, and development of the board: | |||
[https://www.youtube.com/watch?v=LqJ7HhS65po The Tesla Project : 10 Kw Gen 2 Charger] | |||
[https://www.youtube.com/watch?v=ULadBnl7wgM The Tesla Project : Charger Progress] | |||
[https://www.youtube.com/watch?v=mOIgp3QFg78 The Tesla Project : 10kW Charger Charging] | |||
[https://www.youtube.com/watch?v=BG4kYsoHe54 The Tesla Project : More Charger Hacking] | |||
[https://www.youtube.com/watch?v=bPLqXCiArVM The Tesla Project : Charger 10kw Run] | |||
A 15 min intro from a user perspective: https://www.youtube.com/watch?v=ibtr6v1k0cA | |||
==== | ==Common Issues== | ||
=== | *The Tesla chargers are very sensitive to grounding. The case MUST be connected to vehicle 12v ground AND evse earth/ground when charging. [https://openinverter.org/forum/viewtopic.php?p=3890#p3890] | ||
*With V5aB2, If you do NOT use the external CAN bus or are not properly terminated, '''remember to close the solder jumper''' next to R1 under the WiFi module. When in doubt, check the resistance of the CAN bus with all devices off. It should be 60 ohms ideally. If you are not using the external CAN then it should be 120 ohms. | |||
*People had problems with unreliable connectivity between ESP8266 & the charger board [https://openinverter.org/wiki/Olimex_MOD-WIFI-ESP8266#Common_Issues] | |||
*Firmware '''1.09''' and '''1.10''' can lose the CAN map, making the logic board go silent, reset instructions here: [https://openinverter.org/forum/viewtopic.php?p=40617&sid=e2369fea2b502a419f55e5aac10fe169#p40617] | |||
*If a module within the charger is enabled (and all three are enabled by default) then it '''MUST''' see AC and DC voltage when charging starts. If it does not then no current will flow on any module. So, triple check your wiring before starting. It can be easy to mix up the line and neutral wires of the AC input. This will not blow up anything but it won't work either. Mixing up the DC wires is a recipe for a bad time. | |||
*Some chargers are just raised wrong. As covered above, for reasons we don't know, some modules will simply refuse to work properly. Most often this will happen to chargers that were previously used in super charger stations but it can happen to chargers that were pulled from Model S cars as well. There is not yet any known fix for this. If it happens the only current solution is a different charger or you live with slow charging. | |||
*Did you set the D1 enable pin to be high (+12v?) It must be high in '''ANY''' mode in order for charging to start. It is OK to tie it to the +12 incoming power if you are using something like Type2 where charging is controlled by the proximity and control pilot signals. | |||
==== | ==Errata== | ||
Charger Dimensions: 500x300x100mm | |||
More specific dimensions and CAD info here: https://openinverter.org/forum/viewtopic.php?p=3641#p3641CAD | |||
==== | ==Notes== | ||
[[Category:Tesla]] | |||
[[Category:Charger]] | |||
<references /> | |||
Latest revision as of 17:12, 27 February 2026
| HEED DAMIEN'S WARNING:[2] |
TPNs to avoid:
- 1014963-05-B and 1014963-05-C
- 1014963-00-C/E/F/J/K/L
- 1014963-00-C [4]
- 1014963-00-G is likely also good, just wasn't mentioned by name in the referenced thread
Cooling
Charger Connections
| A1 | A2 | A3 | A4 | A5 | B1 | B2 | B3 | B4 | B5 | B6 | |
| OUT2 - AC present | D1 - enable | 12V supply | CANH | Control Pilot | |||||||
| A6 | A7 | A8 | A9 | A10 | B7 | B8 | B9 | B10 | B11 | B12 | |
| OUT1 - HV enable | D2 - 3p | GND | CANL | Proximity |
- housing: 044441-2006
- pins: 043375-3001 (18-20AWG), 043375-0001 (14-16AWG)
- housing: 10-way 19418-0014, 12-way 19418-0026
- pins: 33012-2002 (18-20AWG), 33012-2001 (14-16AWG)
- IPS1-115-01-S-D-PL, SAMTEC - IPS1-115-01-S-D-PL - SOCKET, 2.54MM, 2x15WAY
- NOTE: One of the pins is missing from this connector variant, but according to this forum post, it's OK as long as you solder it in the correct orientation.
- IPS1-115-01-L-D, SAMTEC
- Has all 30 pins.
Programming
- ST-LINK programming utility: https://www.st.com/en/development-tools/stsw-link004.html
- stm32_loader.hex https://openinverter.org/forum/viewtopic.php?f=7&t=1119
Two options:
- Charger_gen2_v5.hex https://github.com/damienmaguire/Tesla-Charger/tree/master/V5/Software/Binary
- openinverter style firmware https://openinverter.org/forum/viewtopic.php?t=1323 (only available via patreon for next few weeks)
External CAN bus
| ID | Direction | Byte 0 | Byte 1 | Byte 2 | Byte 3 | Byte 4 | Byte 5 | Byte 6 | Byte 7 |
| 0x102 | Receive by charger | DC voltage limit MSB | DC voltage limit LSB | DC current set point | ==1 enable charging | SoC | |||
| 0x108 | Transmit by charger | Version=0 | Max DC voltage MSB | Max DC voltage LSB | Max DC current | ||||
| 0x109 | Transmit by charger | Version=0 | DC voltage MSB | DC voltage LSB | DC current | 0 when off, 5 when charging |
- Support for the standard open inverter web interface
- Parameter handling as known from the inverter firmware (see picture)
- Spot value handling like inverter including plotting, gauges, and logging
- Over the air update like inverter
- DC current control
- CAN control as described above
By default all charger kits will have SSID : charger PASSWORD : charger123
Missing IC4 Chip
Registration
Common Issues
- The Tesla chargers are very sensitive to grounding. The case MUST be connected to vehicle 12v ground AND evse earth/ground when charging. [1]
- With V5aB2, If you do NOT use the external CAN bus or are not properly terminated, remember to close the solder jumper next to R1 under the WiFi module. When in doubt, check the resistance of the CAN bus with all devices off. It should be 60 ohms ideally. If you are not using the external CAN then it should be 120 ohms.
- People had problems with unreliable connectivity between ESP8266 & the charger board [2]
- Firmware 1.09 and 1.10 can lose the CAN map, making the logic board go silent, reset instructions here: [3]
- If a module within the charger is enabled (and all three are enabled by default) then it MUST see AC and DC voltage when charging starts. If it does not then no current will flow on any module. So, triple check your wiring before starting. It can be easy to mix up the line and neutral wires of the AC input. This will not blow up anything but it won't work either. Mixing up the DC wires is a recipe for a bad time.
- Some chargers are just raised wrong. As covered above, for reasons we don't know, some modules will simply refuse to work properly. Most often this will happen to chargers that were previously used in super charger stations but it can happen to chargers that were pulled from Model S cars as well. There is not yet any known fix for this. If it happens the only current solution is a different charger or you live with slow charging.
- Did you set the D1 enable pin to be high (+12v?) It must be high in ANY mode in order for charging to start. It is OK to tie it to the +12 incoming power if you are using something like Type2 where charging is controlled by the proximity and control pilot signals.
- ↑ https://teslamotorsclub.com/tmc/posts/6560948/
- ↑ https://openinverter.org/forum/viewtopic.php?t=932
- ↑ https://openinverter.org/forum/viewtopic.php?p=34710#p34710 and also by Lars on June 25th 2024
- ↑ https://openinverter.org/forum/viewtopic.php?p=2030#p2030