Peugeot E-Boxer NMC cells reuse modules.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Peugeot E-Boxer NMC cells reuse modules.
Hi, just joined you all. I live off grid in the UK (25 yrs with a 24KWh FLA set up using Outback inverter charger. 6.5Kw of PV and 3 Kw wind turbine. 24V battery) Also 10KVA gen set on Auto start.
I wish to double my battery capacity and upgrade to a 48 V system.
I have just purchased the complete battery and case from a 2022 plate Boxer-E with just 1000 miles on the clock.
I have dismantled the case and disconnected the modules. So I have 18 modules @ 44V nominal, Each module is 2 packs of 6s2p (in series) so effectivley 12s2p. Module energy 2.74KWh.
I wish for help in using these modules in the simplest and most reliable way. I am a long time user of Outback equipment, for it’s rugged build and reliability and simplicity and ideally would use their kit as I am familiar with their programming and menus etc.
The spec of the Outback VFXR3048E allows for DC charging on a scale from 42 to 68VDC. To support a larger load in the house I would have 2 inverters in parallel which also enables battery charging at a higher rate from a gen set (2X 45ADC).
I could have 9 packs at 44V in parallel. If I have a low volt point for recharge set at 43.2 (3.6V per cell) (30%SOC) and top V for charging at 49.2 (4.1V per cell) then that fits in with the Outback VDC capability.
So my question is can I manage the BMS side of the project using the onboard BMS circuit board, I note cell terminals are welded and the BMS board is an interference fit on a set op pins on the module cells.
Any thoughts please.
I have piccies but have not worked out how to upload them yet.
I wish to double my battery capacity and upgrade to a 48 V system.
I have just purchased the complete battery and case from a 2022 plate Boxer-E with just 1000 miles on the clock.
I have dismantled the case and disconnected the modules. So I have 18 modules @ 44V nominal, Each module is 2 packs of 6s2p (in series) so effectivley 12s2p. Module energy 2.74KWh.
I wish for help in using these modules in the simplest and most reliable way. I am a long time user of Outback equipment, for it’s rugged build and reliability and simplicity and ideally would use their kit as I am familiar with their programming and menus etc.
The spec of the Outback VFXR3048E allows for DC charging on a scale from 42 to 68VDC. To support a larger load in the house I would have 2 inverters in parallel which also enables battery charging at a higher rate from a gen set (2X 45ADC).
I could have 9 packs at 44V in parallel. If I have a low volt point for recharge set at 43.2 (3.6V per cell) (30%SOC) and top V for charging at 49.2 (4.1V per cell) then that fits in with the Outback VDC capability.
So my question is can I manage the BMS side of the project using the onboard BMS circuit board, I note cell terminals are welded and the BMS board is an interference fit on a set op pins on the module cells.
Any thoughts please.
I have piccies but have not worked out how to upload them yet.
-
- Posts: 589
- Joined: Thu Mar 02, 2023 1:30 pm
- Location: Uk
- Has thanked: 295 times
- Been thanked: 82 times
Re: Peugeot E-Boxer NMC cells reuse modules.
Something isn't quite right. If you have 18 modules at 44v each then you'd have a 792V pack if they were in series which is likely.
Please can you upload the pics and also dimensions of the modules?
You can do so by going to the "Full editor" and then scroll to the bottom to upload photos and other media.
Regarding the other stuff I'm not able to help but hopefully others can.
Please can you upload the pics and also dimensions of the modules?
You can do so by going to the "Full editor" and then scroll to the bottom to upload photos and other media.
Regarding the other stuff I'm not able to help but hopefully others can.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
Hello Jacob. Thanks for pointing out my error, caught by terminology. And thanks, I've found the upload as well. Each module is 6s2p 22V nominal. Each module is built paired up in its water cooling pack, so 44VDC, so 9 x pairs of modules is 400V as built.
So what I'm looking for is the simplest way to build a nominal 48V battery and can I re use the integral BMS board, and if so what else would be required, please?
Below is spec for the complete battery
51 KWh.
Pack voltage 400V
Capacity 127.5Ah.
Total cells 216
Battery pack 108s2p
Modules 18
Module energy 2.74kWh
Module nominal 22V
Cells in module 12
Module configuration 6s2p
Format Prismatic.
Cell chemistry Lithium ion NMC
Cell nominal Voltage 3.7V
Standard charge and discharge cut off V 4.2V/2.75.
Cell capacity 62Ah
Battery voltage before dismantling was 388VDC and individual cells measure 3.59
So what I'm looking for is the simplest way to build a nominal 48V battery and can I re use the integral BMS board, and if so what else would be required, please?
Below is spec for the complete battery
51 KWh.
Pack voltage 400V
Capacity 127.5Ah.
Total cells 216
Battery pack 108s2p
Modules 18
Module energy 2.74kWh
Module nominal 22V
Cells in module 12
Module configuration 6s2p
Format Prismatic.
Cell chemistry Lithium ion NMC
Cell nominal Voltage 3.7V
Standard charge and discharge cut off V 4.2V/2.75.
Cell capacity 62Ah
Battery voltage before dismantling was 388VDC and individual cells measure 3.59
-
- Posts: 20
- Joined: Tue Mar 14, 2023 7:11 pm
- Location: Sofia, BG
- Has thanked: 5 times
- Been thanked: 12 times
Re: Peugeot E-Boxer NMC cells reuse modules.
Probably, those are the same modules used in Peugeot e-208 and other cars from the Stellantis group.
The on-board BMS is described here: viewtopic.php?t=2181.
It's possible to reuse it, but it requires some specific hardware for communication (PCB with MAX17841B).
I'm unfamiliar with the Outback inverters and their communication protocol for Li-Ion batteries. I hope it is publicly available.
I and other people on the forum use these modules in complete stack configuration (400VDC), but this requires an HV inverter.
The on-board BMS is described here: viewtopic.php?t=2181.
It's possible to reuse it, but it requires some specific hardware for communication (PCB with MAX17841B).
I'm unfamiliar with the Outback inverters and their communication protocol for Li-Ion batteries. I hope it is publicly available.
I and other people on the forum use these modules in complete stack configuration (400VDC), but this requires an HV inverter.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
So I notice that the 9 modules are all connected daisy chain in series all the way back to the main control module. The daisy chain loom consists of only 4 wires . From this I deduce that the individual modules board must be doing the actual "work" ie balancing cells, etc and the 4 wires are (perhaps) supply power to the individual module boards (sub 9V) red and green/ and the 2 white wires are carrying signals either to or from the module and main control "box".
So simple (stupid) question. If reconnect the daisy chain back together on all 9 modules and reconnect to the main battery control module, will the cells be checked and balanced if required? Power to this main BMS is 12 Vdc from the main car battery?
I only need the simplest control as i would plan to use voltage based signal to trigger ac charging (gen set) and high bat voltage to signal off to the gen set. I don't see that the inverter needs to comm with the bms. I don't need a SOC reading as in an off grid set up the battery is never at a static point. There is always a load, the house; and there can be DC charging 24/7 from solar and wind. And if battery is low the genset just starts automatically and stays on until it gets an off signal. Charging rate/voltage is set in the Inverter/charger.
So simple (stupid) question. If reconnect the daisy chain back together on all 9 modules and reconnect to the main battery control module, will the cells be checked and balanced if required? Power to this main BMS is 12 Vdc from the main car battery?
I only need the simplest control as i would plan to use voltage based signal to trigger ac charging (gen set) and high bat voltage to signal off to the gen set. I don't see that the inverter needs to comm with the bms. I don't need a SOC reading as in an off grid set up the battery is never at a static point. There is always a load, the house; and there can be DC charging 24/7 from solar and wind. And if battery is low the genset just starts automatically and stays on until it gets an off signal. Charging rate/voltage is set in the Inverter/charger.
-
- Posts: 20
- Joined: Tue Mar 14, 2023 7:11 pm
- Location: Sofia, BG
- Has thanked: 5 times
- Been thanked: 12 times
Re: Peugeot E-Boxer NMC cells reuse modules.
I guess that the board over the cell looks like this:
There are four wires between each module, but they are only communication (RX and TX pairs). The cells power the balance PCB.
It's possible to reconnect all modules (18) to the central BMS and to get cell data. Some people try to do this here:
viewtopic.php?t=2675
I tried some time ago and even connected an OBD adapter to the CAN bus, and it's possible to get a lot of data. But I don't know whether the central BMS will balance the cell in this setup.
Indeed, the cells inside are very well-balanced, and you can run a battery without balancing for a long time.
Anyway, you will need some cell monitoring at a minimum, and I think the easiest way is to use an OBD scanner. I can give some directions on how to connect it.
Other solutions that exist require hardware and programming.
There are four wires between each module, but they are only communication (RX and TX pairs). The cells power the balance PCB.
It's possible to reconnect all modules (18) to the central BMS and to get cell data. Some people try to do this here:
viewtopic.php?t=2675
I tried some time ago and even connected an OBD adapter to the CAN bus, and it's possible to get a lot of data. But I don't know whether the central BMS will balance the cell in this setup.
Indeed, the cells inside are very well-balanced, and you can run a battery without balancing for a long time.
Anyway, you will need some cell monitoring at a minimum, and I think the easiest way is to use an OBD scanner. I can give some directions on how to connect it.
Other solutions that exist require hardware and programming.
-
- Posts: 1785
- Joined: Fri Mar 01, 2019 9:15 pm
- Location: Bristol
- Has thanked: 153 times
- Been thanked: 350 times
Re: Peugeot E-Boxer NMC cells reuse modules.
Please get details of the chip, better picture and markings on it.
This looks like some ISO-SPI comms.
This looks like some ISO-SPI comms.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
Hi Yasko, hi Tom. Thank you for your replies. Yes the board over the cells appears to be same/similar to the illistration you provide. See mine below. I have the complete battery pack with all modules and the wiring loom. The daisy chain terminates at what I assume to be the main battery control module. I have removed the cover. The main chip conveniently is marked with black text on black so I can't get a picture, no contrast. I have copied the marks as follows.
INFINEON. TRICORE
SAKTC 275TP/64F200 (WCA I think)
hard to read last line Infineon 14 84 62018.
Yasko, you say that Indeed, the cells inside are very well-balanced, and you can run a battery without balancing for a long time. I have read other peoples posts with similar view. Do you mean that cell balancing is not a required function?
To recap, what I wish to achieve is the most simple of basic functions to maintain the cells in good working order for the rest of their lives. I would envisage monitering high and low battery voltage through the inverter charger with it's auto command to start and stop the genset as dictated.
Not concerned about SOC as in off grid there never is a static SOC. There is always draw on the battery (house load) and most of the time charging from RE sources.
Over temp on cells. I read that this battery could accept 80% charge in 1 hr. I would imagine that might demand a cooling system. The max charge rate I am likely to achieve would be 7Kwh, which might not cause over heating. I could very easily connect up the water cooling jackets on the modules with a temp sensor to run a circulation pump on demand. Or run it as a heater to keep cells warm in mid winter?
Any help or guidance would be much appreciated. I am old and this is new to me. Being old does mean it takes longer to learn new stuff.
INFINEON. TRICORE
SAKTC 275TP/64F200 (WCA I think)
hard to read last line Infineon 14 84 62018.
Yasko, you say that Indeed, the cells inside are very well-balanced, and you can run a battery without balancing for a long time. I have read other peoples posts with similar view. Do you mean that cell balancing is not a required function?
To recap, what I wish to achieve is the most simple of basic functions to maintain the cells in good working order for the rest of their lives. I would envisage monitering high and low battery voltage through the inverter charger with it's auto command to start and stop the genset as dictated.
Not concerned about SOC as in off grid there never is a static SOC. There is always draw on the battery (house load) and most of the time charging from RE sources.
Over temp on cells. I read that this battery could accept 80% charge in 1 hr. I would imagine that might demand a cooling system. The max charge rate I am likely to achieve would be 7Kwh, which might not cause over heating. I could very easily connect up the water cooling jackets on the modules with a temp sensor to run a circulation pump on demand. Or run it as a heater to keep cells warm in mid winter?
Any help or guidance would be much appreciated. I am old and this is new to me. Being old does mean it takes longer to learn new stuff.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
-
- Posts: 1785
- Joined: Fri Mar 01, 2019 9:15 pm
- Location: Bristol
- Has thanked: 153 times
- Been thanked: 350 times
Re: Peugeot E-Boxer NMC cells reuse modules.
We want to IC markings on the module boards not the main controller.
- uhi22
- Posts: 939
- Joined: Mon Mar 14, 2022 3:20 pm
- Location: Ingolstadt/Germany
- Has thanked: 136 times
- Been thanked: 529 times
Re: Peugeot E-Boxer NMC cells reuse modules.
These ones:
Github: http://github.com/uhi22 --- Patreon: https://www.patreon.com/uhi22
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
I'll try again but by eye, these 3 items appear to have no markings visible. They are coated with a varnish like treatment which renders them opaque. I will try to find some magnification device and come back with any info obtained. Thank you for your interest. Andy
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
I realise that "looking the same" is not very scientific, but the thread here appears to be covering the same battery modules set up. viewtopic.php?p=35581#p35581
For the sake of discussion. IF the modules I have are "the same" what will be my 1st step to repurpose the battery, albeit re connected as a LV battery not 400Vdc.
For the sake of discussion. IF the modules I have are "the same" what will be my 1st step to repurpose the battery, albeit re connected as a LV battery not 400Vdc.
- EV_Builder
- Posts: 1200
- Joined: Tue Apr 28, 2020 3:50 pm
- Location: The Netherlands
- Has thanked: 17 times
- Been thanked: 35 times
- Contact:
Re: Peugeot E-Boxer NMC cells reuse modules.
This BMS is available. You can configure them the way you like.
(But practical is obviously per 6S).
(But practical is obviously per 6S).
Converting an Porsche Panamera
see http://www.wdrautomatisering.nl for bespoke BMS modules.
see http://www.wdrautomatisering.nl for bespoke BMS modules.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
I plan to put them in 2s8P to give 44v and use an Outback inverter charger. The Outbacks nominal 48V settings have a wide enough range to accommodate the lower nominal battery voltage. I will have 2 inverters in parallel to give larger supply and charging capacity.
Sorry, which BMS system was that.
Sorry, which BMS system was that.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
Sorry missed your link at first glance. Found it now; that looks really useful, great.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
I wondered if any one who is reuseing these modules has a view on the integral cooling system and whether in a static off grid set up the active cooling is needed. I would not expect to be charging or discharging at a greater rate than 7Kwh .
It would be fairly simple to plumb the modules and connect to a water pump and radiator to dissipate heat, triggered by a signal from the onboard PCB. Is this overkill, are the cells likely to overheat in the aboce scenario?
The battery will be located in a purpose made cabinet in a large dry ventilated building. Heating can be provided in the cabinet if the ambient temp drops to freezing.
It would be fairly simple to plumb the modules and connect to a water pump and radiator to dissipate heat, triggered by a signal from the onboard PCB. Is this overkill, are the cells likely to overheat in the aboce scenario?
The battery will be located in a purpose made cabinet in a large dry ventilated building. Heating can be provided in the cabinet if the ambient temp drops to freezing.
-
- Posts: 20
- Joined: Tue Mar 14, 2023 7:11 pm
- Location: Sofia, BG
- Has thanked: 5 times
- Been thanked: 12 times
Re: Peugeot E-Boxer NMC cells reuse modules.
Based on my observations, liquid cooling is not needed for this application. This battery can handle 10kW without problems, and the temperature increases by a few degrees. Here, I talk about 400V configuration, but with proper reconfiguration, this will be the same for an LV application.
Regarding your previous question about cell balancing, a friend has been running a similar battery (Pegeout e208) without balancing for over a year, and the cell difference stays around 20mV. The battery was balanced manually before connection to the inverter.
Anyway, I recommend a suitable controller for battery monitoring. Let's not forget that these cells are Li-Ion, not Lead-acid, and require more attention.
Regarding your previous question about cell balancing, a friend has been running a similar battery (Pegeout e208) without balancing for over a year, and the cell difference stays around 20mV. The battery was balanced manually before connection to the inverter.
Anyway, I recommend a suitable controller for battery monitoring. Let's not forget that these cells are Li-Ion, not Lead-acid, and require more attention.
-
- Posts: 11
- Joined: Sat Mar 09, 2024 9:46 am
- Been thanked: 1 time
Re: Peugeot E-Boxer NMC cells reuse modules.
Thanks for your input Yasko. I was of the opinion that the water cooling would not be required with my relativley low level charge/discharge, nice to have a second opinion.
I plan to be in touch with http://www.wdrautomatisering.nl/ as suggested by "EV Builder" for the BMS controller. My son is a senior software engineer and I've just discovered, conversant with both UART and SDI protocols so I've got him lined up to help with this project. Saves any more wear and tear on my old (70+ ) brain.
Thank you.
I plan to be in touch with http://www.wdrautomatisering.nl/ as suggested by "EV Builder" for the BMS controller. My son is a senior software engineer and I've just discovered, conversant with both UART and SDI protocols so I've got him lined up to help with this project. Saves any more wear and tear on my old (70+ ) brain.
Thank you.