16-cell BMS: Difference between revisions
| Line 329: | Line 329: | ||
==== Charge Curve ==== | ==== Charge Curve ==== | ||
The initial approach was to assign a certain charge current to points in the SoC curve. This method can be skewed if the SoC calculation is off for some reason. The new method deploys 3 CC/CV regulators. This was copied from oberving VWs charge curve of the MEB cars. The first regulator has the highest charge current and aims for a voltage typically around 3.9V for many NMC chemistries. When current drops below the CC value of the second regulator then that one is used, aiming for a higher voltage of typically 4V. And finally the 3rd regulator takes over aiming for the charge end voltage of typically 4.2V. When setting all 3 to the same values a simple CC/CV curve is generated. | |||
==== Voltage limits ==== | ==== Voltage limits ==== | ||
Revision as of 12:40, 6 June 2024
Communication
All configuration, queries and firmware updates are done via the CAN bus. There is no independent web interface like known from e.g. the inverter. However there is a solution to connect an ESP32 via CAN and then have the known web interface [2] or you can use Dave Fiddes "oic" tool for the command line[3]. It is important to know that the main module has node-id 10 and the subsequent ones 10+i (i index of submodule, so 1st submodule has node-id 1). The base node id can be configured to start at something else than 10.
Apart from that the modules output periodic CAN messages depending on their role. The base address for cyclic messages defaults to 0x1F4 and can be changed by modifying pdobase on the main module. pdobase is ignored on the sub modules.
All modules output on ID 501 (0x1F5) + i
| start | length | item | description |
| 0 | 13 | umin | minimum cell voltage of module i |
| 16 | 13 | umax | maximum cell voltage of module i |
| 30 | 2 | counter | counts from 0-3 (anti-freeze) |
| 32 | 13 | uavg | average cell voltage of module i |
| 48 | 8 | tempmin | Minimum temp +40 on module i |
| 56 | 8 | tempmax | Maximum temp +40 on module i |
In addition the main module outputs on id 500 (0x1F4)
| 0 | 11 | chargelim | maximum charge current in A |
| 11 | 11 | dischargelim | maximum discharge current in A |
| 22 | 10 | soc | Pack soc in 0.1% |
| 32 | 16 | idcavg | Averaged current reading of last 1s in 0.1A - signed! |
| 48 | 10 | utotal | Total pack voltage in V |
| 62 | 2 | counter | counts from 0-3 (anti-freeze) |
Reading individual cell voltages
Cell voltages are only available via CAN SDO from the module that measures them. So voltages 1-16 must be queried from the first (main) module, 17-32 from the 2nd (1st submodule) and so on. With Dave Fiddes tool this translates to:
oic -n 3 dumpall #dumps all values including cell voltages from 1st module
oic -n 4 dumpall #same for second module
oic -n 4 read u0 #Read first cell voltage of second module
For querying voltages say in your arduino sketch you'll need to acquire every voltage separately by sending and receiving SDO messages
0x60A#0x40 idhigh 0x21 idlow 0 0 0 0
0x60A#0x40 0x07 0x21 0xD6 0 0 0 0
0x58A#0x43 0x07 0x21 0xD6 0xD0 0xED 0x01 0
The next cell would be on 0x7D7 and the last on 0x7E5. The next 16 voltages are then queried from node id 0x60B.
Configuration Parameters
There is currently a limited set of parameters which will be extended as the software grows. This table always reflects the latest git commit. Check the page history for previous versions.
These are the parameters of v0.16.B
| BMS | |||||
| gain | uV/dig | 1 | 1000 | 586 | Scaling factor from ADC digits to mV |
| correction0 | ppm | -10000 | 10000 | -1250 | The first two and the last channel have slightly different topology and need their own correction factor |
| correction1 | ppm | -10000 | 10000 | 1500 | |
| correction15 | ppm | -10000 | 10000 | 1000 | |
| numchan | 1 | 16 | 16 | Number of cells connected to the module | |
| balmode | 0 | 3 | 0 | Balancing mode
0=No balancing 1=Only bump up low cells 2=Only dissipate high cells 3=Do both | |
| ubalance | mV | 0 | 4500 | 4500 | Voltage above which top balancing is started |
| idlewait | s | 0 | 100000 | 60 | Number of seconds to wait after stop of current flow to measure unloaded cell voltage und start balancing |
| Battery Characteristics | |||||
| dischargemax | A | 1 | 2047 | 200 | Maximum discharge current |
| nomcap | Ah | 0 | 1000 | 100 | Nominal capacity |
| icc1 | A | 1 | 2000 | 50 | Maximum charge current of empty battery |
| icc2 | A | 1 | 2000 | 30 | Maximum charge current of roughly half-charged battery |
| icc3 | A | 1 | 2000 | 20 | Maximum charge current of rather full battery |
| ucv1 | mV | 3000 | 4500 | 3900 | First constant voltage set point. Transition to next one when dropping below icc2 |
| ucv2 | mV | 3000 | 4500 | 4000 | Second constant voltage set point. Transition to next one when dropping below icc3 |
| ucellmax | mV | 3000 | 4500 | 4200 | Third constant voltage set point and maximum cell voltage |
| ucellmin | mV | 1000 | 4500 | 3300 | Minimum loaded cell voltage. Discharge limit is dropped to stay above this value |
| chargeXsoc | % | 0 | 100 | Percentage of charge current at soc X. In between two points charge current is interpolated | |
| Sensor Setup | |||||
| idcgain | dig/A | -1000 | 1000 | 10 | Gain (or actually division factor) of current sensor |
| idcofs | dig | -4095 | 4095 | 0 | 0A offset |
| idcmode | 0 | 3 | 0 | Current sensor mode 0=Off, 1=Single Ended ADC, 2=Differential ADC, 3=ISA current shunt | |
| tempsns | -1 | 3 | -1 | Temperature sensor -1=Off, 0=JCurve, 1=KTY81, 2=PT1000, 3=LeafBMS | |
| Communication | |||||
| pdobase | 0 | 2047 | 500 | base COB Id for cyclic messages. Main module uses pdobase and pdobase+1, 1st submodule uses pdobase+2 and so on | |
| sdobase | 0 | 63 | 10 | base node ID for SDO queries. Main module uses sdobase, 1st submodule sdobase+1 and so on | |
Operation
Calculating current limits
Charge Curve
Voltage limits
Voltage limits are enforced via a P-regulator. I.e. as we approach the upper or lower voltage limit current is cut back to stay away from the limits until it reaches 0A. The upper and lower limit is configurable
Temperature limits
These are not enforced yet. High temperature will cut back both charge and discharge current whereas low temperature will only cut back charge current.
Energy limits