Added tuning guide Damien posted from Arbor333 |
| Line 54: | Line 54: | ||
|'''Description''' | |'''Description''' | ||
| colspan="6" |'''Motor''' | | colspan="6" |'''Motor (FOC)''' | ||
|curkp | |||
|0 | |||
|20000 | |||
|64 | |||
|Current controller proportional gain | |||
|curkp | |||
|0 | |||
|100000 | |||
|20000 | |||
|Current controller integral gain | |||
|curkifrqgain | |||
|dig/Hz | |||
|0 | |||
|1000 | |||
|50 | |||
|Current controllers integral gain frequency coefficient | |||
|fwkp | |||
|-10000 | |||
|0 | |||
|-100 | |||
|Cross comparison field weakening controller gain | |||
|dmargin | |||
|dig/Hz | |||
|-10000 | |||
|0 | |||
|-2000 | |||
|Margin for residual torque producing current (so field weakening current doesn't use up the entire amplitude) | |||
|syncadv | |||
|dig/Hz | |||
| -100 | |||
|100 | |||
|10 | |||
|Shifts "syncofs" downwards/upwards with frequency | |||
| colspan="6" |'''Motor (sine)''' | |||
|boost | |boost | ||
| Line 76: | Line 120: | ||
|0 | |0 | ||
|Nominal voltage for fweak and boost. fweak and boost are scaled to the actual dc voltage. 0=don't scale | |Nominal voltage for fweak and boost. fweak and boost are scaled to the actual dc voltage. 0=don't scale | ||
|fpconst | |fpconst | ||
| Line 111: | Line 141: | ||
|3 | |3 | ||
|Slip frequency at maximum throttle | |Slip frequency at maximum throttle | ||
| colspan="6" |'''Motor (common)''' | |||
|polepairs | |polepairs | ||
| Line 140: | Line 172: | ||
|0=single channel encoder, 1=quadrature encoder, | |0=single channel encoder, 1=quadrature encoder, | ||
2=quadrature /w index pulse, | 2=quadrature /w index pulse, | ||
3=SPI (deprecated) | 3=SPI (deprecated), | ||
4=Resolver | 4=Resolver, | ||
5=sin/cos chip | |||
|fmin | |fmin | ||
| Line 184: | Line 217: | ||
|0 | |0 | ||
|Phase shift of sine wave after receiving index pulse | |Phase shift of sine wave after receiving index pulse | ||
|snsm | |snsm | ||
Revision as of 12:25, 18 February 2020
The inverter can be adapted to many kinds of motors, battery packs and driver preferences by changing parameters.
Motor Parameters
Example: boost=1700
<figure-inline class="mw-default-size"><figure-inline><figure-inline>
</figure-inline></figure-inline></figure-inline>
With our illustration motor fweak=355/230*50=77Hz. fweak can be configured lower than that resulting in more torque at the low end.
Inverter Parameters
Parameter Reference
set
to change it. Type
get
to get the current value.
| Motor (FOC) | |||||
| curkp | 0 | 20000 | 64 | Current controller proportional gain | |
| curkp | 0 | 100000 | 20000 | Current controller integral gain | |
| curkifrqgain | dig/Hz | 0 | 1000 | 50 | Current controllers integral gain frequency coefficient |
| fwkp | |||||
| 0 | |||||
| Cross comparison field weakening controller gain | |||||
| dmargin | dig/Hz | ||||
| 0 | |||||
| Margin for residual torque producing current (so field weakening current doesn't use up the entire amplitude) | |||||
| syncadv | dig/Hz | -100 | 100 | 10 | Shifts "syncofs" downwards/upwards with frequency |
| Motor (sine) | |||||
| boost | dig | 0 | 37813 | 1700 | 0 Hz Boost in digit. 1000 digit ~ 2.5% |
| fweak | Hz | 0 | 400 | 67 | Frequency where V/Hz reaches its peak |
| udcnom | V | 0 | 1000 | 0 | Nominal voltage for fweak and boost. fweak and boost are scaled to the actual dc voltage. 0=don't scale |
| fpconst | Hz | 0 | 400 | 400 | Frequency where slip frequency is derated to form a constant power region. Only has an effect when < fweak |
| fslipmin | Hz | 0 | 100 | 1 | Slip frequency at minimum throttle |
| fslipmax | Hz | 0 | 100 | 3 | Slip frequency at maximum throttle |
| Motor (common) | |||||
| polepairs | 1 | 16 | 2 | Pole pairs of motor (4-pole motor: 2 pole pairs) | |
| respolepairs | 1 | 16 | 1 | Pole pairs of resolver | |
| encflt | 0 | 16 | 4 | Filter constant between pulse encoder and speed calculation. Makes up for slightly uneven pulse distribution | |
| encmode | 0 | 4 | 0 | 0=single channel encoder, 1=quadrature encoder,
| fmin | Hz | 0 | 400 | 1 | Below this frequency no voltage is generated |
| fmax | Hz | 0 | 400 | 200 | At this frequency slip is commanded 0 to avoid further acceleration |
| numimp | Imp/rev | 8 | 8192 | 60 | Pulse encoder pulses per turn |
| dirchrpm | rpm | 0 | 2000 | 100 | Motor speed at which direction change is allowed |
| dirmode | 0 | 1 | 1 | 0=button (momentary pulse selects forward/reverse), 1=switch (forward or reverse signal must be constantly high) | |
| syncofs | dig | 0 | 65535 | 0 | Phase shift of sine wave after receiving index pulse |
| snsm | 2 | 3 | 2 | Motor temperature sensor. 2=KTY83, 3=KTY84 | |
| Inverter | |||||
| pwmfrq | 0 | 3 | 2 | PWM frequency. 0=17.6kHz, 1=8.8kHz, 2=4.4kHz, 3=2.2kHz. Needs PWM restart | |
| pwmpol | 0 | 1 | 0 | PWM polarity. 0=active high, 1=active low. DO NOT PLAY WITH THIS!
| deadtime | dig | 0 | 255 | 28 | Deadtime between highside and lowside pulse. 28=800ns, 56=1.5µs. Not always linear, consult STM32 manual. Needs PWM restart |
| ocurlim | A | -65535 | 65535 | 100 | Hardware over current limit. RMS-current times sqrt(2) + some slack |
| minpulse | dig | 0 | 4095 | 1000 | Narrowest or widest pulse, all other mapped to full off or full on, respectively |
| il1gain | dig/A | 0 | 4095 | 4.7 | Digits per A of current sensor L1 |
| il2gain | dig/A | 0 | 4095 | 4.7 | Digits per A of current sensor L2 |
| udcgain | dig/V | 0 | 4095 | 6.15 | Digits per V of DC link |
| udcofs | dig | 0 | 4095 | 0 | DC link 0V offset |
| udclim | V | 0 | 1000 | 540 | High voltage at which the PWM is shut down |
| snshs | 0 | 1 | 0 | Heatsink temperature sensor. 0=JCurve, 1=Semikron | |
| Derating | |||||
| bmslimhigh | % | 0 | 100 | 50 | Positive throttle limit on BMS under voltage |
| bmslimlow | % | -100 | 0 | -1 | Regen limit on BMS over voltage |
| udcmin | V | 0 | 1000 | 450 | Minimum battery voltage |
| udcmax | V | 0 | 1000 | 520 | Maximum battery voltage |
| iacmax | A | 0 | 5000 | 5000 | Maximum peak AC current |
| ifltrise | dig | 0 | 32 | 10 | Controls how quickly slip and amplitude recover. The greater the value, the slower |
| ifltfall | dig | 0 | 32 | 3 | Controls how quickly slip and amplitude are reduced on over current. The greater the value, the slower |
| idcmax | A | 0 | 5000 | 5000 | Maximum DC input current |
| idcmin | A | -5000 | 0 | -5000 | Maximum DC output current (regen) |
| throtmax | % | 0 | 100 | 100 | Throttle limit |
| Charger | |||||
| chargemode | 0 | 4 | 0 | 0=Off, 3=Boost, 4=Buck | |
| chargecur | 0 | 50 | 0 | Charge current setpoint. Boost mode: charger INPUT current. Buck mode: charger output current | |
| chargekp | 0 | 100 | 80 | Charge controller gain. Lower if you have oscillation, raise if current set point is not met | |
| chargeflt | 0 | 10 | 8 | Charge current filtering. Raise if you have oscillations | |
| chargemax | % | 0 | 99 | 90 | Charge mode duty cycle limit. Especially in boost mode this makes sure you don't overvolt you IGBTs if there is no battery connected. |
| Throttle | |||||
| potmin | dig | 0 | 4095 | 0 | Value of "pot" when pot isn't pressed at all |
| potmax | dig | 0 | 4095 | 4095 | Value of "pot" when pot is pushed all the way in |
| pot2min | dig | 0 | 4095 | 4095 | Value of "pot2" when regen pot is in 0 position |
| pot2max | dig | 0 | 4095 | 4095 | Value of "pot2" when regen pot is in full on position |
| potmode | 0 | 2 | 0 | 0=Pot 1 is throttle and pot 2 is regen strength preset,
1=Pot 2 is proportional to pot 1 (redundance) 2=Throttle controlled via CAN | |
| throtramp | %/10ms | 0 | 100 | 100 | Max positive throttle slew rate |
| throtramprpm | rpm | 0 | 20000 | 20000 | No throttle ramping above this speed |
| ampmin | % | 0 | 100 | 10 | Minimum relative sine amplitude |
| slipstart | % | 10 | 100 | 50 | % positive throttle travel at which slip is increased |
| Regen | |||||
| brknompedal | % | -100 | 0 | -50 | Foot on break pedal regen torque |
| brkpedalramp | %/10ms | 1 | 100 | 100 | Ramp speed when entering regen. E.g. when you set brkmax to 20% and brkpedal to -60% and brkpedalramp to 1, it will take 400ms to arrive at brake force of -60% |
| brknom | % | 0 | 100 | 30 | Regen padel travel |
| brkmax | % | 0 | 100 | 30 | Foot-off regen torque |
| brkout | % | -100 | -1 | -50 | Activate brake light output at this amount of braking force |
| brkrampstr | Hz | 0 | 400 | 10 | Below this frequency the regen torque is reduced linearly with the frequency |
| Automation | |||||
| idlespeed | rpm | -100 | 1000 | -100 | Motor idle speed. Set to -100 to disable idle function. When idle speed controller is enabled, brake pedal must be pressed on start. |
| idlethrotlim | % | 0 | 100 | 50 | Throttle limit of idle speed controller |
| idlemode | 0 | 1 | 0 | Motor idle speed mode. 0=always run idle speed controller, 1=only run it when brake pedal is released, 2=like 1 but only when cruise switch is on | |
| speedkp | Hz | 0 | 100 | 1 | Speed controller gain (Cruise and idle speed). Decrease if speed oscillates. Increase for faster load regulation |
| cruisemode | 0 | 1 | 0 | 0=button (set when button pressed, reset with brake pedal), 1=switch (set when switched on, reset when switched off or brake pedal) | |
| speedflt | dig | 0 | 16 | 1 | Filter before cruise controller |
| Contactor Control | |||||
| udcsw | V | 0 | 1000 | 330 | Voltage at which the DC contactor is allowed to close |
| udcswbuck | V | 0 | 1000 | 540 | Voltage at which the DC contactor is allowed to close in buck charge mode |
| tripmode | 0 | 2 | 0 | What to do with relays at a shutdown event. 0=All off, 1=Keep DC switch closed, 2=close precharge relay | |
| Auxillary PWM | |||||
| pwmfunc | 0 | 2 | 0 | Quantity that controls the PWM output. 0=tmpm, 1=tmphs, 2=speed | |
| pwmgain | dig/C | 0 | 65535 | 100 | Gain of PWM output |
| pwmofs | dig | -65535 | 65535 | 0 | Offset of PWM output, 4096=full on |
| Communication | |||||
| canspeed | 0 | 3 | 0 | Baud rate of CAN interface 0=250k, 1=500k, 2=800k, 3=1M | |
| canperiod | 0 | 1 | 0 | 0=send configured CAN messages every 100ms, 1=every 10ms | |
| Testing | |||||
| fslipspnt | Hz | -100 | 100 | 0 | Slip setpoint in mode 2. Written by software in mode 1 |
| ampnom | % | 0 | 100 | 0 | Nominal amplitude in mode 2. Written by software in mode 1 |
get
get il1,il2,udc
| Name | Unit | Description |
| version | Firmware version | |
| opmode | Operating mode. 0=Off, 1=Run, 2=Manual_run, 3=Boost, 4=Buck, 5=Sine, 6=2 Phase sine | |
| udc | V | DC link voltage |
| uac | V | Calculated AC voltage |
| idc | A | Calculated DC current |
| il1 | A | AC current L1 |
| il2 | A | AC current L2 |
| il1rms | A | RMS current L1 |
| il2rms | A | RMS current L2 |
| boostcalc | A | DC link adjusted boost setting |
| fweakcalc | A | DC link adjusted fweak setting |
| fstat | Hz | Stator frequency |
| speed | rpm | Motor speed |
| amp | dig | Sine amplitude, 37813=max |
| pot | dig | Pot value, 4095=max |
| pot2 | dig | Regen Pot value, 4095=max |
| potnom | % | Scaled pot value, 0 accel |
| dir | Rotation direction. -1=REV, 0=Neutral, 1=FWD | |
| tmphs | °C | Heatsink temperature |
| tmpm | °C | Motor temperature |
| uaux | °C | Auxiliary voltage (i.e. 12V system). Measured on pin 11 (mprot) |
| din_cruise | Cruise Control. This pin activates the cruise control with the current speed. Pressing again updates the speed set point. | |
| din_start | State of digital input "start". This pin starts inverter operation | |
| din_brake | State of digital input "brake". This pin sets maximum regen torque (brknompedal). Cruise control is disabled. | |
| din_mprot | State of digital input "motor protection switch". Shuts down the inverter when =0 | |
| din_forward | Direction forward | |
| din_reverse | Direction backward | |
| din_emcystop | State of digital input "emergency stop". Shuts down the inverter when =0 | |
| din_ocur | Over current detected | |
| din_bms | BMS over voltage/under voltage | |
| cpuload | % | CPU load for everything except communication |
Tuning Guide