m Changed brkmax to negative. https://openinverter.org/forum/viewtopic.php?t=4285 |
| Line 615: | Line 615: | ||
|100 | |100 | ||
|100 | |100 | ||
|Ramp speed when entering regen. E.g. when you set brkmax to 30% and regenramp to 1, it will take 300ms to arrive at brake force of -60% | |Ramp speed when entering regen. E.g. when you set brkmax to -30% and regenramp to 1, it will take 300ms to arrive at brake force of -60% | ||
|brknom / regentravel | |brknom / regentravel | ||
| Line 626: | Line 626: | ||
|brkmax / offthrotregen | |brkmax / offthrotregen | ||
| | | -100 | ||
| | | 0 | ||
|30 | | -30 | ||
|Foot-off throttle regen torque | |Foot-off throttle regen torque | ||
Revision as of 12:54, 25 October 2023
Motor Parameters
Example: boost=1700
Inverter Parameters
Parameter Reference
set param <value>
to change it. Type
get param
to get the current value.
| Motor (FOC) | |||||
| iqkp | 0 | 20000 | 64 | Current controller proportional gain. Low inductance/resistance motors need less, high inductance/resistance motors more | |
| idkp | 0 | 20000 | 64 | Same as above but often a little higher then iqkp | |
| curki | 0 | 100000 | 20000 | Current controller integral gain (id and iq) | |
| vlimflt | 0 | 16 | 10 | Amplitude limiting field weakening filter | |
| vlimmargin | 0 | 10000 | 2500 | Field weakening is brought in at modmax-vlimmargin. Increase if you get short bursts of unwanted regen at speed | |
| fwcurmax | -1000 | 0 | -100 | Maximum field weakening current. Must be set to critical current of motor (TODO: link forum). Set to 0 for disabling field weakening | |
| lqminusld | mH | 0 | 1000 | 0 | Difference between d and q axis inductance. The higher, the more d-current is brought in for additional reluctance torque |
| fluxlinkage | mWeber | 0 | 1000 | 90 | Magnetic link between rotor and stator, shapes MTPA curve |
| syncadv | dig/Hz | 0 | 65535 | 10 | Shifts "syncofs" downwards/upwards with frequency. Must be set so that ud remains at 0 when coasting below field weakening speed. SUPER DANGEROUS! Setting it wrong can cause unwanted acceleration. |
| curkifrqgain | dig/Hz | 0 | 1000 | 50 | Current controllers integral gain frequency coefficient (deprecated, removed) |
| ffwstart | Hz | 0 | 1000 | 200 | Starting point of field weakening controller. Below that frequency it is disabled, above it its gain is increased proportional to frequency and hits fwkp at fmax. (deprecated, removed in latest release) |
| Motor (sine) | |||||
| boost | dig | 0 | 37813 | 1700 | 0 Hz Boost in digit. 1000 digit ~ 2.5% |
| fweakstrt | Hz | 0 | 1000 | 400 | Fweak value at potnom < 35%. Can improve low speed stability and reduce oscillation when set higher than fweak. Set equal to fweak to disable. |
| fweak | Hz | 0 | 400 | 67 | Frequency where V/Hz reaches its peak |
| fconst | Hz | 0 | 400 | 400 | Maximum slip is increased from fslipmax to fslipconstmax as frequency approaches this value. Only effective when greater than fweak. |
| udcnom | V | 0 | 1000 | 0 | Nominal voltage for fweak and boost. fweak and boost are scaled to the actual dc voltage. 0=don't scale |
| fslipmin | Hz | 0 | 100 | 1 | Slip frequency at minimum throttle |
| fslipmax | Hz | 0 | 100 | 3 | Slip frequency at maximum throttle |
| fslipconstmax | Hz | 0 | 10 | 5 | Slip frequency at maximum throttle and fconst. Set equal to fslipmax to disable. |
| fmin | Hz | 0 | 400 | 1 | Below this frequency no voltage is generated |
| Motor (common) | |||||
| polepairs | 1 | 16 | 2 | Pole pairs of motor (e.g. 4-pole motor: 2 pole pairs) | |
| respolepairs | 1 | 16 | 1 | Pole pairs of resolver (normally same as polepairs of motor, but sometimes 1) | |
| sincosofs | dig | 0 | 4096 | 2048 | Mid point of sin/cos chip |
| encflt | 0 | 16 | 4 | Filter constant between pulse encoder and speed calculation. Makes up for slightly uneven pulse distribution | |
| encmode | 0 | 4 | 0 | 0=single channel encoder, 1=quadrature encoder,
| fmax | Hz | 0 | 400 | 200 | At this frequency rev limiting kicks in |
| numimp | Imp/rev | 8 | 8192 | 60 | Pulse encoder pulses per turn |
| dirchrpm | rpm | 0 | 2000 | 100 | Motor speed at which direction change is allowed |
| dirmode | 0 | 1 | 1 | 0=button (momentary pulse selects forward/reverse), 1=switch (forward or reverse signal must be constantly high) | |
| syncofs | dig | 0 | 65535 | 0 | Phase shift of sine wave after receiving index pulse |
| snsm | 2 | 3 | 2 | Motor temperature sensor. 12=KTY83, 13=KTY84, 14=Leaf, 15=KTY81 | |
| Inverter | |||||
| pwmfrq | 0 | 3 | 2 | PWM frequency. 0=17.6kHz, 1=8.8kHz, 2=4.4kHz, 3=2.2kHz. Needs PWM restart | |
| pwmpol | 0 | 1 | 0 | PWM polarity. 0=active high, 1=active low. DO NOT PLAY WITH THIS!
| deadtime | dig | 0 | 255 | 28 | Deadtime between highside and lowside pulse. 28=800ns, 56=1.5µs. Not always linear, consult STM32 manual. Needs PWM restart |
| ocurlim | A | -65535 | 65535 | 100 | Hardware over current limit. RMS-current times sqrt(2) + some slack. Set negative if il1gain and il2gain are negative. |
| minpulse | dig | 0 | 4095 | 1000 | Narrowest or widest pulse, all other mapped to full off or full on, respectively |
| il1gain | dig/A | 0 | 4095 | 4.7 | Digits per A of current sensor L1 |
| il2gain | dig/A | 0 | 4095 | 4.7 | Digits per A of current sensor L2 |
| udcgain | dig/V | 0 | 4095 | 6.15 | Digits per V of DC link |
| udcofs | dig | 0 | 4095 | 0 | DC link 0V offset |
| udclim | V | 0 | 1000 | 540 | High voltage at which the PWM is shut down |
| snshs | 0 | 1 | 0 | Heatsink temperature sensor. 0=JCurve, 1=Semikron, 2=MBB600, 3=KTY81, 4=PT1000, 5=NTCK45+2k2, 6=Leaf | |
| pinswap | 0 | 7 | 0 | Swap pins (only "FOC" software). Multiple bits can be set. 1=Swap Current Inputs, 2=Swap Resolver sin/cos, 4=Swap PWM output 1/3
0001 = 1 Swap Currents ony 0010 = 2 Swap Resolver only 0011 = 3 Swap Resolver and Currents 0100 = 4 Swap PWM 1 and 3 only 0101 = 5 Swap PWM 1 and 3 and Currents 0110 = 6 Swap PWM 1 and 3 and Resolver 0111 = 7 Swap PWM 1 and 3 and Resolver and Currents 1xxx likewise with PWM 2 and 3 | |
| Derating | |||||
| bmslimhigh | % | 0 | 100 | 50 | Positive throttle limit on BMS under voltage |
| bmslimlow | % | -100 | 0 | -1 | Regen limit on BMS over voltage |
| udcmin | V | 0 | 1000 | 450 | Minimum battery voltage |
| udcmax | V | 0 | 1000 | 520 | Maximum battery voltage |
| iacmax | A | 0 | 5000 | 5000 | Maximum peak AC current |
| idcmax | A | 0 | 5000 | 5000 | Maximum DC input current |
| idckp | dig | 0.1 | 20 | 2 | Proportional rate of DC current derating |
| idcmin | A | -5000 | 0 | -5000 | Maximum DC output current (regen) |
| throtmax | % | 0 | 100 | 100 | Throttle limit |
| throtmin | % | -100 | 0 | -100 | Throttle regen limit |
| ifltrise | dig | 0 | 32 | 10 | Controls how quickly slip and amplitude recover. The greater the value, the slower |
| ifltfall | dig | 0 | 32 | 3 | Controls how quickly slip and amplitude are reduced on over current. The greater the value, the slower |
| Charger | |||||
| chargemode | 0 | 4 | 0 | 0=Off, 3=Boost, 4=Buck | |
| chargecur | 0 | 50 | 0 | Charge current setpoint. Boost mode: charger INPUT current. Buck mode: charger output current | |
| chargekp | 0 | 100 | 80 | Charge controller proportional gain. Lower if you have oscillation, raise to get best power factor. | |
| chargeki | 0 | 100 | 10 | Charge controller integral gain. | |
| chargeflt | 0 | 10 | 8 | Charge current filtering. Raise if you have oscillations | |
| chargepwmin | % | 0 | 99 | 0 | Lowest charge mode duty cycle. This is needed for synchronous converters like in the Prius Gen2 where the lower IGBT is also active in buck mode and actually boosts the battery voltage into the bus capacitor when duty cycle is low. |
| chargepwmax | % | 0 | 99 | 90 | Charge mode duty cycle limit. Especially in boost mode this makes sure you don't overvolt you IGBTs if there is no battery connected. |
| Throttle | |||||
| potmin | dig | 0 | 4095 | 0 | Value of "pot" when pot isn't pressed at all |
| potmax | dig | 0 | 4095 | 4095 | Value of "pot" when pot is pushed all the way in |
| pot2min | dig | 0 | 4095 | 4095 | Value of "pot2" when regen pot is in 0 position |
| pot2max | dig | 0 | 4095 | 4095 | Value of "pot2" when regen pot is in full on position |
| potmode | 0 | 2 | 0 | 0=Pot 1 is throttle and pot 2 is regen strength preset
1=Pot 2 is proportional to pot 1 (redundancy) 2=Throttle/regen controlled via CAN (like 0) 3=Throttle via CAN with redundancy (like 1) | |
| throtramp | %/10ms | 0 | 100 | 100 | Max positive throttle slew rate |
| throtramprpm | rpm | 0 | 20000 | 20000 | No throttle ramping above this speed |
| ampmin | % | 0 | 100 | 10 | Minimum relative sine amplitude (only "sine" software) |
| slipstart | % | 10 | 100 | 50 | % positive throttle travel at which slip is increased (only "sine" software) |
| throtcur | A/% | -10 | 10 | 1 | Motor current per % of throttle travel (only "FOC" software) |
| Regen | |||||
| brknompedal / brakeregen | % | -100 | 0 | -50 | Foot on brake pedal regen torque |
| regenramp | %/10ms | 0.1 | 100 | 100 | Ramp speed when entering regen. E.g. when you set brkmax to -30% and regenramp to 1, it will take 300ms to arrive at brake force of -60% |
| brknom / regentravel | % | 0 | 100 | 30 | Range of throttle pedal travel allocated to regen |
| brkmax / offthrotregen | % | -100 | 0 | -30 | Foot-off throttle regen torque |
| brkcruise / cruiseregen | % | -100 | 0 | -30 | Maximum regen of cruise control |
| brkrampstr / regenrampstr | Hz | 0 | 400 | 10 | Below this frequency the regen torque is reduced linearly with the frequency |
| brkout / brklightout | % | -100 | -1 | -50 | Activate brake light output at this amount of braking force |
| Automation | |||||
| idlespeed | rpm | -100 | 1000 | -100 | Motor idle speed. Set to -100 to disable idle function. When idle speed controller is enabled, brake pedal must be pressed on start. |
| idlethrotlim | % | 0 | 100 | 50 | Throttle limit of idle speed controller |
| idlemode | 0 | 1 | 0 | Motor idle speed mode. 0=always run idle speed controller, 1=only run it when brake pedal is released, 2=like 1 but only when cruise switch is on | |
| speedkp | Hz | 0 | 100 | 1 | Speed controller gain (Cruise and idle speed). Decrease if speed oscillates. Increase for faster load regulation |
| speedflt | dig | 0 | 16 | 1 | Filter before cruise controller |
| cruisemode | 0 | 1 | 0 | 0=button (set when button pressed, reset with brake pedal), 1=switch (set when switched on, reset when switched off or brake pedal) | |
| Contactor Control | |||||
| udcsw | V | 0 | 1000 | 330 | Voltage at which the DC contactor is allowed to close |
| udcswbuck | V | 0 | 1000 | 540 | Voltage at which the DC contactor is allowed to close in buck charge mode |
| tripmode | 0 | 2 | 0 | What to do with relays at a shutdown event. 0=All off, 1=Keep DC switch closed, 2=close precharge relay | |
| bootprec | 0 | 1 | 0 | Engage precharge relay in boot loader. Introduced for enabling Prius Gen3 DC/DC converter when precharge relay is released. Use together with tripmode=2 | |
| Auxillary PWM | |||||
| pwmfunc | 0 | 2 | 0 | Quantity that controls the PWM output. 0=tmpm, 1=tmphs, 2=speed | |
| pwmgain | dig/C | 0 | 65535 | 100 | Gain of PWM output |
| pwmofs | dig | -65535 | 65535 | 0 | Offset of PWM output, 4096=full on |
| Communication | |||||
| canspeed | 0 | 3 | 0 | Baud rate of CAN interface 0=250k, 1=500k, 2=800k, 3=1M | |
| canperiod | 0 | 1 | 0 | 0=send configured CAN messages every 100ms, 1=every 10ms | |
| nodeid | 1 | 63 | 1 | Node ID for CAN SDO messages and for selective enabling of UART when sharing one ESP8266 module between multiple processors. | |
| Testing | |||||
| fslipspnt | Hz | -100 | 100 | 0 | Slip setpoint in mode 2. Written by software in mode 1 |
| ampnom | % | 0 | 100 | 0 | Nominal amplitude in mode 2. Written by software in mode 1 |
Spot values
get
get il1,il2,udc
| Name | Unit | Description |
| version | Firmware version | |
| hwver | Hardware version | |
| opmode | Operating mode. 0=Off, 1=Run, 2=Manual_run, 3=Boost, 4=Buck, 5=Sine, 6=2 Phase sine | |
| lasterr | Last error message | |
| udc | V | DC link voltage |
| uac | V | Calculated AC voltage |
| idc | A | Calculated DC current |
| il1 | A | AC current L1 |
| il2 | A | AC current L2 |
| il1rms | A | RMS current L1 |
| il2rms | A | RMS current L2 |
| ilmax | A | Calculated max of il1, il2, il3 |
| boostcalc | A | DC link adjusted boost setting |
| fweakcalc | A | DC link adjusted fweak setting |
| fstat | Hz | Stator frequency |
| speed | rpm | Motor speed |
| cruisespeed | rpm | Motor RPM set point for cruise control if cruisemode=CAN |
| turns | Number of turns the motor completed since power up | |
| amp | dig | Sine amplitude, 37813=max |
| angle | ° | Motor rotor angle, 0-360°. When using the SINE software, the slip is added to the rotor position. |
| pot | dig | Pot value, 4095=max |
| pot2 | dig | Regen Pot value, 4095=max |
| potnom | % | Scaled pot value, 0 accel |
| dir | Rotation direction. -1=REV, 0=Neutral, 1=FWD | |
| tmphs | °C | Heatsink temperature |
| tmpm | °C | Motor temperature |
| uaux | V | Auxiliary voltage (i.e. 12V system). Measured on pin 11 (mprot) |
| pwmio | raw state of PWM outputs at power up | |
| canio | Digital IO bits received via CAN | |
| din_cruise | Cruise Control. This pin activates the cruise control with the current speed. Pressing again updates the speed set point. | |
| din_start | State of digital input "start". This pin starts inverter operation | |
| din_brake | State of digital input "brake". This pin sets maximum regen torque (brknompedal). Cruise control is disabled. | |
| din_mprot | State of digital input "motor protection switch". Shuts down the inverter when =0 | |
| din_forward | Direction forward | |
| din_reverse | Direction backward | |
| din_emcystop | State of digital input "emergency stop". Shuts down the inverter when =0 | |
| din_ocur | Over current detected | |
| din_bms | BMS over voltage/under voltage | |
| cpuload | % | CPU load for everything except communication |
Tuning Guide