Added tuning guide Damien posted from Arbor333
Line 54: Line 54:
|'''Description'''
|'''Description'''
| colspan="6" |'''Motor'''
| colspan="6" |'''Motor (FOC)'''
|curkp
|0
|20000
|64
|Current controller proportional gain
|curkp
|0
|100000
|20000
|Current controller integral gain
|curkifrqgain
|dig/Hz
|0
|1000
|50
|Current controllers integral gain frequency coefficient
|fwkp
|-10000
|0
|-100
|Cross comparison field weakening controller gain
|dmargin
|dig/Hz
|-10000
|0
|-2000
|Margin for residual torque producing current (so field weakening current doesn't use up the entire amplitude)
|syncadv
|dig/Hz
| -100
|100
|10
|Shifts "syncofs" downwards/upwards with frequency
| colspan="6" |'''Motor (sine)'''
|boost
|boost
Line 76: Line 120:
|0
|0
|Nominal voltage for fweak and boost. fweak and boost are scaled to the actual dc voltage. 0=don't scale
|fwkp
|0
|10000
|1
|Inverter MTPA (maximum torque per amp) gain
|frqfac
|dig/Hz
| -10000
|10000
|10
|PI controller help to reach appropriate output at higher frequencies. 0=No Help
|fpconst
|fpconst
Line 111: Line 141:
|3
|3
|Slip frequency at maximum throttle
| colspan="6" |'''Motor (common)'''
|polepairs
|polepairs
Line 140: Line 172:
|0=single channel encoder, 1=quadrature encoder,
2=quadrature /w index pulse,
3=SPI (deprecated)
3=SPI (deprecated),
4=Resolver
4=Resolver,
5=sin/cos chip
|fmin
|fmin
Line 184: Line 217:
|0
|0
|Phase shift of sine wave after receiving index pulse
|syncadv
|dig/Hz
| -100
|100
|0
|snsm
|snsm
Revision as of 12:25, 18 February 2020
The inverter can be adapted to many kinds of motors, battery packs and driver preferences by changing parameters.
Motor Parameters
Example: boost=1700
<figure-inline class="mw-default-size"><figure-inline><figure-inline></figure-inline></figure-inline></figure-inline>
With our illustration motor fweak=355/230*50=77Hz. fweak can be configured lower than that resulting in more torque at the low end.
Inverter Parameters
Parameter Reference
set
to change it. Type
get
to get the current value.
Motor (FOC)
curkp 0 20000 64 Current controller proportional gain
curkp 0 100000 20000 Current controller integral gain
curkifrqgain dig/Hz 0 1000 50 Current controllers integral gain frequency coefficient
fwkp
0
dmargin dig/Hz
0
syncadv dig/Hz -100 100 10 Shifts "syncofs" downwards/upwards with frequency
Motor (sine)
fpconst Hz 0 400 400 Frequency where slip frequency is derated to form a constant power region. Only has an effect when < fweak
Motor (common)
polepairs 1 16 2 Pole pairs of motor (4-pole motor: 2 pole pairs)
respolepairs 1 16 1 Pole pairs of resolver
encmode 0 4 0 0=single channel encoder, 1=quadrature encoder,
fmax Hz 0 400 200 At this frequency slip is commanded 0 to avoid further acceleration
dirmode 0 1 1 0=button (momentary pulse selects forward/reverse), 1=switch (forward or reverse signal must be constantly high)
snsm 2 3 2 Motor temperature sensor. 2=KTY83, 3=KTY84
Needs PWM restart
ocurlim A -65535 65535 100 Hardware over current limit. RMS-current times sqrt(2) + some slack
minpulse dig 0 4095 1000 Narrowest or widest pulse, all other mapped to full off or full on, respectively
snshs 0 1 0 Heatsink temperature sensor. 0=JCurve, 1=Semikron
Derating
Charger
chargekp 0 100 80 Charge controller gain. Lower if you have oscillation, raise if current set point is not met
chargemax % 0 99 90 Charge mode duty cycle limit. Especially in boost mode this makes sure you don't overvolt you IGBTs if there is no battery connected.
Throttle
potmode 0 2 0 0=Pot 1 is throttle and pot 2 is regen strength preset,
1=Pot 2 is proportional to pot 1 (redundance) 2=Throttle controlled via CAN
ampmin % 0 100 10 Minimum relative sine amplitude
slipstart % 10 100 50 % positive throttle travel at which slip is increased
Regen
brknompedal % -100 0 -50 Foot on break pedal regen torque
brkpedalramp %/10ms 1 100 100 Ramp speed when entering regen. E.g. when you set brkmax to 20% and brkpedal to -60% and brkpedalramp to 1, it will take 400ms to arrive at brake force of -60%
brknom % 0 100 30 Regen padel travel
brkmax % 0 100 30 Foot-off regen torque
brkout % -100 -1 -50 Activate brake light output at this amount of braking force
brkrampstr Hz 0 400 10 Below this frequency the regen torque is reduced linearly with the frequency
Automation
idlemode 0 1 0 Motor idle speed mode. 0=always run idle speed controller, 1=only run it when brake pedal is released, 2=like 1 but only when cruise switch is on
Contactor Control
udcsw V 0 1000 330 Voltage at which the DC contactor is allowed to close
Auxillary PWM
Communication
Testing
get
get il1,il2,udc
Name Unit Description
version Firmware version
udc V DC link voltage
uac V Calculated AC voltage
idc A Calculated DC current
il1 A AC current L1
il2 A AC current L2
il1rms A RMS current L1
il2rms A RMS current L2
boostcalc A DC link adjusted boost setting
fweakcalc A DC link adjusted fweak setting
fstat Hz Stator frequency
speed rpm Motor speed
pot dig Pot value, 4095=max
potnom % Scaled pot value, 0 accel
dir Rotation direction. -1=REV, 0=Neutral, 1=FWD
tmphs °C Heatsink temperature
tmpm °C Motor temperature
uaux °C Auxiliary voltage (i.e. 12V system). Measured on pin 11 (mprot)
din_forward Direction forward
Tuning Guide
