Thanks! I will try to guesstimate the amount of energy that needs to be absorbed. I’ll keep you posted.
SDU parameter tuning - major failure - can't select drive gear
Re: SDU parameter tuning - major failure - can't select drive gear
Re: SDU parameter tuning - major failure - can't select drive gear
Ok, I’m placing my tvs+resistor on the dc side. If possible, would it be better to connect the between phases?
- johu
- Site Admin
- Posts: 5792
- Joined: Thu Nov 08, 2018 10:52 pm
- Location: Kassel/Germany
- Has thanked: 158 times
- Been thanked: 1028 times
- Contact:
Re: SDU parameter tuning - major failure - can't select drive gear
God no DC bus!
Support R/D and forum on Patreon: https://patreon.com/openinverter - Subscribe on odysee: https://odysee.com/@openinverter:9
Re: SDU parameter tuning - major failure - can't select drive gear
Hi Peter could you share the details of your connection. When you say TVS I guess you mean TVS - Transient Voltage suppressor diode?
Subscribe on YouTube: https://www.youtube.com/user/peakon28
- Peter
- Posts: 310
- Joined: Fri Dec 14, 2018 9:07 pm
- Location: North West Lancs, UK
- Been thanked: 8 times
Re: SDU parameter tuning - major failure - can't select drive gear
Hi Peakon28. Suggest a high power Varistor in series with a resistor. My max pack voltage is 330v so in my case the Varistor must be able to handle 330v DC continuous without problems. The Varistor will start conducting above that value and I am doing some tests again with it. The type I have has a max voltage of 590v DC. Its all a matter of trial and test but as mentioned before Tripmode 1 is a MUST. Not sure how high regen voltage can become so consider that also.
-
- Posts: 1801
- Joined: Sun Apr 03, 2022 1:57 pm
- Has thanked: 102 times
- Been thanked: 347 times
Re: SDU parameter tuning - major failure - can't select drive gear
Not sure whether I've misunderstood something, and don't want to seem negative, but I can't see the varistor/resistor arrangement doing much.
On varistors and transzorbs the slope resistance is a fairly critical metric and adding a 25R series resistor just ruins it. Say you are trying to dump just 50A though the two, the resistor will drop 50A x 25R = 1250V (with the varistor voltage on top of that), still more than enough to kill the inverter.
The best protection is the tripmode, except for emergencies the breaker must NOT open while there is still current flowing in the motor!
On varistors and transzorbs the slope resistance is a fairly critical metric and adding a 25R series resistor just ruins it. Say you are trying to dump just 50A though the two, the resistor will drop 50A x 25R = 1250V (with the varistor voltage on top of that), still more than enough to kill the inverter.
The best protection is the tripmode, except for emergencies the breaker must NOT open while there is still current flowing in the motor!
- Peter
- Posts: 310
- Joined: Fri Dec 14, 2018 9:07 pm
- Location: North West Lancs, UK
- Been thanked: 8 times
Re: SDU parameter tuning - major failure - can't select drive gear
Hi Pete9008. Tripmode is the best solution agreed. But as a second line of defence my aim is to catch a spike voltage before it gets over 600v and kills the SDU power stage. I tried with just varistors before and as the spike voltage increased above the varistor continuous DC voltage the varistors went into self destruct mode, quite a dramatic event. Saved my inverter though My thought (rightly or wrongly) was to have the series resistor act as a load so the power would be dissipated across that too and save the varistors doing all the dissipation and hopefully survive to work another day. As long as there is a method to absorb a spike should the worse case scenario appear that would be my goal. However I would gladly bow to your greater knowledge and appreciate any advice please
-
- Posts: 1801
- Joined: Sun Apr 03, 2022 1:57 pm
- Has thanked: 102 times
- Been thanked: 347 times
Re: SDU parameter tuning - major failure - can't select drive gear
A varistor alone would work as it will clamp the voltage but as you say if it can not handle the power it will self destruct. It may save the inverter though.
The trouble is that if you add a series resistor the inverter sees the voltage across the combination of the varistor and the resistor. The varistor will top out at say 590V but you have to add to that whatever voltage drops across the resistor. If you have too much current through them (which is likely if the motor was taking current as it has nowhere else to go) the added voltage across the resistor (1250V in the above example) will easily put you back in the inverter killing range. The varistor may survive though!
Edit - unfortunately most of my knowledge on how not to destroy things has been gained by accidentally destroying things (in this particular case a few industrial measurement boards, followed by a scope while investigating, were the unlucky pieces of equipment)!
The trouble is that if you add a series resistor the inverter sees the voltage across the combination of the varistor and the resistor. The varistor will top out at say 590V but you have to add to that whatever voltage drops across the resistor. If you have too much current through them (which is likely if the motor was taking current as it has nowhere else to go) the added voltage across the resistor (1250V in the above example) will easily put you back in the inverter killing range. The varistor may survive though!
Edit - unfortunately most of my knowledge on how not to destroy things has been gained by accidentally destroying things (in this particular case a few industrial measurement boards, followed by a scope while investigating, were the unlucky pieces of equipment)!
- Peter
- Posts: 310
- Joined: Fri Dec 14, 2018 9:07 pm
- Location: North West Lancs, UK
- Been thanked: 8 times
Re: SDU parameter tuning - major failure - can't select drive gear
Hi Pete9008. Its funny how destruction makes us think harder
-
- Posts: 1801
- Joined: Sun Apr 03, 2022 1:57 pm
- Has thanked: 102 times
- Been thanked: 347 times
Re: SDU parameter tuning - major failure - can't select drive gear
Always say you learn a lot more when you fail than you do when you succeed - still not nice at the time though!
Remember also having to build a custom rig to reproduce the several 1000A surges so that the new improved protection circuit could be tested - and that self destructed to when we pushed it to the limit while trying to find the limits of the new protection circuit.
I'm afraid I can't think of a guaranteed circuit to protect the SDU if the breaker opens, there is just too much stored energy to deal with. Your straight varistor approach is probably the only real option but with the caveat that if it ever has to operate it will likely fail violently!
Remember also having to build a custom rig to reproduce the several 1000A surges so that the new improved protection circuit could be tested - and that self destructed to when we pushed it to the limit while trying to find the limits of the new protection circuit.
I'm afraid I can't think of a guaranteed circuit to protect the SDU if the breaker opens, there is just too much stored energy to deal with. Your straight varistor approach is probably the only real option but with the caveat that if it ever has to operate it will likely fail violently!
- EV_Builder
- Posts: 1199
- Joined: Tue Apr 28, 2020 3:50 pm
- Location: The Netherlands
- Has thanked: 16 times
- Been thanked: 33 times
- Contact:
Re: SDU parameter tuning - major failure - can't select drive gear
Maybe the solution lies in a current sensor and a relais and HVIL style circuitry. So we don't open a breaker but we do limb the engine and thus the current flow with out opening a breaker.