CAN communication
The Revision 2 main board supports CAN communication. The CAN bus can be used for configuration and for obtaining values like voltages, input states etc. The CAN messages are configurable and can be adjusted to be compatible with existing equipment.
Since firmware 3.75 throttle and digital inputs can be controlled via CAN.
After firmware 5.27.R throttle, digital inputs, cruise speed and regen preset are no longer freely mappable due to safety concerns, see below.
Be aware that all CAN mapping uses decimal numbers. So COB ID 0x123 must be entered as 291
Inverter control via CAN - new!
As discussed here[1] the CAN communication was redesigned to improve operational safety. This will become effective with the first official release after 5.27.R
Now there is a fixed mapping for pot, pot2, canio, cruisespeed and regenpreset along with some alive counters and a CRC.
The COB Id is still freely configurable and defaults to 0x3F. It is advised to use a low ID value as low IDs have priority on the bus over high Ids.
The mapping is as follows [startbit, endbit]:
- pot[0:11]
- pot2[12:23]
- canio[24:29]
- cuise[24]
- start[25]
- brake[26]
- forward[27]
- reverse[28]
- bms[29]
- canrun1[30:31]
- cruisespeed[32:45]
- canrun2[46:47]
- regenpreset[48:55]
- cancrc[56:63]
pot is the value of the first throttle channel and its range is configured with potmin/potmax as before. pot2 is the value of the second throttle channel, its range configured via pot2min/pot2max and we strongly recommend to use dual channel throttle pedals and setting potmode to CanDual (or DualChannel if you choose to connect the throttle directly to the inverter). We also recommand to set up your throttle in a way that doesn't use the full range from 0-4095 but leaves at least 500 digit at either end (so 500-3600) to be able to detect cable issues between throttle and VCU (short to Vcc, loss of GND and other wire breaks)
cruisespeed is the setpoint for the speed control loop in rpm with a maximum value of 16383 rpm. Only applied if the cruise and forward bit is also set and the brake bit is reset.
regenpreset is a value from 0-100% that controls how much of your configured regen (offthrotregen or brakeregen) is actually applied
canrun1/2 are simple message counters that count from 0-3 and indicate that the message producer doesn't just send the same, stale, content over and over again.
cancrc is an 8-bit CRC, the last byte of the STM32 integrated CRC32 generator. It spans over all 8 bytes where the crc byte is set to 0. If you're on a non-STM32 platform you can use this C-implementation[2]
Controlling throttle via CAN - deprecated!
If you want to send the throttle and regen magnitude commands via CAN rather then via analog inputs you have to set "potmode" to "CAN" (=2). Next you have to map a CAN message to pot and optionally pot2. So say you have a digital throttle that sends values from 0 to 1000 for 0 to 100% travel on CAN-Id 100 in the first two bytes.
- Configure potmin=0 and potmax=1000
- Map CAN message to pot: can rx pot 100 0 16 1
CAN messages must be received every 500ms, otherwise throttle times out and is set to 0.
Controlling Digital IO via CAN - deprecated
6 signals, namely cruise, start, brake, forward, backward and bms can be controlled via CAN. The CAN message is ORed to the physical inputs so you can have mixed signals also. Digital CAN IO doesn't need to be explicitely configured, it works as soon as you map a CAN message to "canio". "canio" is bit-encoded:
- Bit 0: cruise
- Bit 1: start
- Bit 2: brake
- Bit 3: forward
- Bit 4: reverse
- Bit 5: bms
So say you have a BMS that transmits an over/under voltage bit on CAN Id 200, 2nd data bit
can rx canio 200 2 1 1024
Note the 1024x gain that shifts the bit into the correct position (5 fraction bits plus 5th data bit). In this case all other IOs remain traditional, only BMS is controlled via CAN. Note that you cannot map multiple CAN messages onto "canio" as they would overwrite each other.
If you have a managed to mangle all 6 bits into one message, say CAN Id 300, first 6 bits the mapping is done like so
can rx canio 300 0 6 32
The same timeout mechanism is used as for throttle control, so after 500ms with no message the CAN-mapped inputs are assumed off. Traditional inputs remain unaffected.
Setting and reading parameters via SDO
The abbreviation SDO is taken from the CANOpen protocol. It assigns a certain meaning to the 8 data bits of a CAN frame.
Note that SDO semantics (cmd) were changed since version 5.20.R of the inverter firmware. Old cmd value is in ()
| Purpose | CAN-Id | Byte 1 (Cmd) | Bytes 2-3 (Index) | Byte 4 (Subindex) | Bytes 5-8 (Data) |
| Set Value | 0x601 | 0x23 (0x40) | 0x2000 | Value Index | Value x 32 |
| Set Value Reply | 0x581 | 0x60 (0x23) | 0x2000 | Value Index | Value x 32 |
| Get Value | 0x601 | 0x40 (0x22) | 0x2000 | Value Index | don't care |
| Get Value Reply | 0x581 | 0x43 | 0x2000 | Value Index | Value x 32 |
| Map Value TX to COB ID yyy | 0x601 | 0x23 (0x40) | 0x3yyy | Value Index | Byte 5: bit offset, Byte 6: bit length, Bytes 7,8: scaling |
| Map Value RX to COB ID yyy | 0x601 | 0x23 (0x40) | 0x4yyy | Value Index | Byte 5: bit offset, Byte 6: bit length, Bytes 7,8: scaling |
| Abort - invalid index | 0x581 | 0x80 | Index of request | Value Index | Abort Code = 0x06020000 |
| Abort - value out of range | 0x581 | 0x80 | Index of request | Value Index | Abort Code = 0x06090030 |
| Set Param | 0x601 | 0x23 (0x40) | 0x21xx xx=MSB UID | Param UID LSB | Value x 32 |
| Set Param Reply | 0x581 | 0x60 (0x23) | 0x21xx xx=MSB UID | Param UID LSB | Value x 32 |
| Get Param | 0x601 | 0x40 (0x22) | 0x21xx xx=MSB UID | Param UID LSB | don't care |
| Get Param Reply | 0x581 | 0x43 | 0x21xx xx=MSB UID | Param UID LSB | Value x 32 |
The value index must be determined by counting the output of the list command. E.g. "boost" at the very top has index 0, potnom has index 77. The indexes can change over firmware versions as new parameters are added somewhere in between.
The Get/Set Param commands use the unique parameter identifier assigned to each savable parameter. These do not vary between firmware versions. Only savable parameters not spot values can be read and written by these commands.
Examples
0x601 # 0x40 0x00 0x20 0x00 0 0 0 0 Get value of "boost"
0x601 # 0x23 0x00 0x20 0x01 0x80 0x0C 0 0 Set "fweak" to 100Hz (0xC80=3200 because scaled by 32)
0x601 # 0x23 0xAA 0x31 0x01 0x08 0x10 1 0 Map value of fweak to COB ID 0x1AA, starting at bit 8, stretching 16 bits, scaled by 1
0x601 # 0x40 0x10 0x20 0x0D 0 0 0 0 Get value of "pwmfrq" on any firmware version or build (0x0D = 13 from the PARAM_ENTRY() for "pwmfrq" in param_prj.h)
Mapping values to arbitrary CAN messages
Values can be mapped into a certain bit range of the 64 payload bits of a CAN message. They can either be read from the message or sent via a message. To do so enter
can tx udc 123 0 16 10
This maps the value of udc to a CAN message with id 123 bits 0..15 (start at bit 0, span over 16 bits) with a gain of 10.
can tx din_forward 123 24 1 1
would map the pin state of the forward input to bit 24 of CAN message with id 123.
If you want to clear all messages, type
can clear
If you want to remove only a specific signal (starting version 4.18.R) type
can del <name>
To save your can map simply type "save".
Mapping Values through the web interface
Value can also be mapped through the web interface.
- CAN Id
- This is the Can Id assigned to the message. Remember, all CAN mapping uses decimal numbers. So ID 0x123 must be entered as 291. Here is a converter to help: https://www.rapidtables.com/convert/number/hex-to-decimal.html
- Position
- This is where in the 64 bit length of the CAN message the data should start.
- Bits
- How many bits are assigned to send the data.
- Gain
- This applies the internal scaling. Pre FW v5.27 this is fixed point (integers only). FW v5.27 and later is floating point (decimals allowed).
- Your gain needs to be opposite of the receiving end's scaling. For example, the Speedhut EV gauges list a scaling of 0.1, meaning they apply that to incoming messages, so you need to transmit with a gain of 10.
- Map to CAN
- TX to tell the control board to transmit the data onto the CANBUS
- RX to tell the control board to expect to receive this data from the CANBUS
Limits
- A maximum of 10 messages can be defined
- Per message a maximum of 8 values can be mapped (50 total over all messages in FW v5.27 and later)
- a value can not span across the 32-bit boundary, i.e. it must be fully contained in the first or second 32 bits of the message. E.g. "can tx udc 123 16 32 10" is not allowed
- A value can span maximum 32 bits
Endianness
CAN messages sent to, or received from the inverter are Little-endian.
If you are sending or receiving messages containing multi-byte values then the byte order must be taken into account.
PC Tool
A PC based tool called openinverter_can_tool exists to query and control openinverter systems over CAN bus with a supported CAN interface adapter.